I know some of you are curious about the power outage Friday 
night.  Here is the official report from facilities.

>X-Sieve: CMU Sieve 2.3
>Delivered-To: rissman at stanford.edu
>X-Mailer: QUALCOMM Windows Eudora Version
>Date: Mon, 10 Dec 2007 10:18:04 -0800
>To: bm-zoneall at bonair.stanford.edu
>From: George Sandoval <georges at bonair.stanford.edu>
>X-PMX-Version:, Antispam-Engine:,
>         Antispam-Data: 2007.12.10.100412
>X-PerlMx-Spam: Gauge=IIIIIII, Probability=7%, Report='HTML_NO_HTTP 0.1,
>         __ANY_QUALCOMM_MUA 0, __C230066_P5 0, __CT 0,
>         __SANE_MSGID 0, __TAG_EXISTS_HTML 0'
>Subject: FW: Campus Power Outage 12/7/07
>X-BeenThere: bm-zoneall at fac-mailgate.stanford.edu
>X-Mailman-Version: 2.1.5
>Sender: bm-zoneall-bounces at fac-mailgate.stanford.edu
>Building Managers, for your reference, attached is information from 
>the Stanford Utilities Department regarding the campus-wide power 
>outage this past weekend....
>>-----Original Message-----
>>From: Dean Murray [ mailto:deanm at bonair.stanford.edu]
>>Sent: Monday, December 10, 2007 9:52 AM
>>To: Mike Goff
>>Subject: Campus Power Outage 12/7/07
>>Importance: High
>>Campus Power/Steam/Chilled Water Outage 12/7/07-12/8/07
>>At 11:48 PM on Friday, December 7th Stanford University experienced a campus
>>wide power outage affecting most of campus and the Central Plant.
>>The cause of the power outage was a 12,000 volt equipment failure in
>>the Cardinal CoGen at the Central Energy Facility.
>>The loss of power caused both steam and chilled water systems to trip
>>The exact sequence of events is under investigation.
>>Electrical Power Systems:
>>At 2:02AM, 12/8/07 (Saturday Morning) all campus power was restored.
>>Steam Systems:
>>The backup boilers were energized and steam service was restored to the
>>Hospital and Med School
>>about 12:45 am with some intermittant pressure issues until 3 am.
>>Steam pressure was fully restored to the Campus buildings by 6 am.
>>Chiled Water:
>>The Chilled Water System was restored to operation at 5 am when the power
>>was restored to